Moveoff
Добавлено: 05 июл 2015, 23:25
компонент moveoff
только обратил на него внимание...
до конца еще не понял как он работает ,поэтому оставлю здесь по нему информацию
описание
есть примеры с sim конфигов и видео автора:
MOVEOFF
NAME
SYNOPSIS
DESCRIPTION
EXAMPLES
FUNCTIONS
PINS
LICENSE
NAME
moveoff − Component for Hal-only offsets
SYNOPSIS
loadrt moveoff [count=N|names=name1[,name2...]] [personality=P,P,...]
DESCRIPTION
The moveoff component is used to offset joint positions using custom Hal connections. Implementing an offset-while-program-is-paused functionality is supported with appropriate connections for the input pins. Nine joints are supported.
The axis offset pin values (offset-in-M) are continuously applied (respecting limits on value, velocity, and acceleration) to the output pins (offset-current-M, pos-plusoffset-M, fb-minusoffset-M) when both enabling input pins (apply-offsets and move-enable) are TRUE. The two enabling inputs are anded internally. A warning pin is set and a message issued if the apply-offsets pin is deasserted while offsets are applied. The warning pin remains TRUE until the offsets are removed or the apply-offsets pin is set.
Typically, the move-enable pin is connected to external controls and the apply-offsets pin is connected to halui.program.is-paused (for offsets only while paused) or set to TRUE (for continuously applied offsets).
Applied offsets are automatically returned to zero (respecting limits) when either of the enabling inputs is deactivated. The zero value tolerance is specified by the epsilon input pin value.
Waypoints are recorded when the moveoff componenent is enabled. Waypoints are managed with the waypoint-sample-secs and waypoint-threshold pins. When the backtrack-enable pin is TRUE, the auto-return path follows the recorded waypoints. When the memory available for waypoints is exhausted, offsets are frozen and the waypoint-limit pin is asserted. This restriction applies regardless of the state of the backtrack-enable pin. An enabling pin must be deasserted to allow a return to the original (non-offset position).
Backtracking through waypoints results in slower movement rates as the moves are point-to-point respecting velocity and acceleration settings. The velocity and acceleration limit pins can be managed dynamically to control offsets at all times.
When backtrack-enable is FALSE, the auto-return move is NOT coordinated, each axis returns to zero at its own rate. If a controlled path is wanted in this condition, each axis should be manually returned to zero before deasserting an enabling pin.
The waypoint-sample-secs, waypoint-threshold, and epsilon pins are evaluated only when the component is idle.
The offsets-applied output pin is provided to indicate the current state to a GUI so that program resumption can be managed. If the offset(s) are non-zero when the apply-offsets pin is deasserted (for example when resuming a program when offsetting during a pause), offsets are returned to zero (respecting limits) and an Error message is issued.
Caution: If offsets are enabled and applied and the machine is turned off for any reason, any external Hal logic that manages the enabling pins and the offset-in-M inputs is responsible for their state when the machine is subsequently turned on again.
This Hal-only means of offsetting is typically not known to LinuxCNC nor available in GUI preview displays. No protection is provided for offset moves that exceed soft limits managed by LinuxCNC. Since soft limits are not honored, an offset move may encounter hard limits (or CRASH if there are no limit switches). Use of the offset-min-M and offset-max-M inputs to limit travel is recommended. Triggering a hard limit will turn off the machine -- see Caution above.
The offset-in-M values may be set with inifile settings, controlled by a GUI, or managed by other Hal components and connections. Fixed values may be appropriate in simple cases where the direction and amount of offset is well-defined but a control method is required to deactivate an enabling pin in order to return offsets to zero. GUIs may provide means for users to set, increment, decrement, and accumulate offset values for each axis and may set offset-in-M values to zero before deasserting an enabling pin.
The default values for accel, vel, min, max, epsilon, waypoint-sample-secs, and waypoint-threshold may not be suitable for any particular application. This Hal component is unaware of limits enforced elsewhere by LinuxCNC. Users should test usage in a simulator application and understand all hazards before use on hardware.
The module personality item sets the number of joints supported (default==3, maximum is 9).
Use of the names= option for naming is required for compatibilty with the gui provided as scripts/moveoff_gui:
 loadrt moveoff names=mv personality=number_of_joints
man moveoff_gui for more information
EXAMPLES
Example simulator configs that demonstrate the moveoff component and a simple gui (scripts/moveoff_gui) are located in configs/sim/axis/moveoff. The axis gui is used for the demonstrations and the configs can be adapted for other guis like touchy and gscreen. An example with the touchy gui is provided in configs/sim/touchy/ngcgui/.
FUNCTIONS
moveoff.N.read-inputs (requires a floating-point thread)
Read all inputs
moveoff.N.write-outputs (requires a floating-point thread)
Write computed offset outputs (offset-current-M, pos-plusoffset-M, fb-minusoffset-M). All other outputs are updated by read-inputs()
PINS
moveoff.N.power-on bit in
Connect to motion.motion-enabled
moveoff.N.move-enable bit in
Enable offsets (Enabling requires apply-offset TRUE also)
moveoff.N.apply-offsets bit in
Enable offsets (Enabling requires move-enable TRUE also)
moveoff.N.backtrack-enable bit in (default: 1)
Enable backtrack on auto-return
moveoff.N.epsilon float in (default: 0.0005)
When enabling pins are deactivated, return to un-offsetted position within epsilon units. Warning: values that are too small in value may cause overshoot, A minimum value of 0.0001 is silently enforced
moveoff.N.waypoint-threshold float in (default: 0.02)
Minimum distance (in a single axis) for a new waypoint
moveoff.N.waypoint-sample-secs float in (default: 0.02)
Minimum sample interval (in seconds) for a new waypoint
moveoff.N.warning bit out
Set TRUE if apply-offsets is deasserted while offset-applied is TRUE
moveoff.N.offset-applied bit out
TRUE if one or more offsets are applied
moveoff.N.waypoint-limit bit out (default: 0)
Indicates waypoint limit reached (motion ceases), an enabling pin must be deasserted to initiate return to original position
moveoff.N.waypoint-ct s32 out
Waypoint count (for debugging)
moveoff.N.waypoint-percent-used s32 out
Percent of available waypoints used
moveoff.N.offset-in-M float in (M=0..personality)
Joint offset input value
moveoff.N.pos-M float in (M=0..personality)
Joint position (typ: axis.0.motor-pos-cmd)
moveoff.N.fb-M float in (M=0..personality)
Joint feedback (typ from encoder and input to pid controller (pid.feedback))
moveoff.N.offset-current-M float out (M=0..personality)
Joint offset current value
moveoff.N.pos-plusoffset-M float out (M=0..personality)
Computed joint position plus offset (typically connect to pid command input)
moveoff.N.fb-minusoffset-M float out (M=0..personality)
Computed Joint feedback minus offset (typically connected to axis.0.motor-pos-fb
moveoff.N.offset-vel-M float in (M=0..personality) (default: 10)
Joint offset velocity limit
moveoff.N.offset-accel-M float in (M=0..personality) (default: 100)
Joint offset acceleration limit
moveoff.N.offset-min-M float in (M=0..personality) (default: -1e20)
Minimum limit for applied joint offset (typ negative)
moveoff.N.offset-max-M float in (M=0..personality) (default: 1e20)
Maximum limit for applied offset (typ positive)
moveoff.N.dbg-waypoint-limit-test bit in
Debug input to test with limited number of waypoints
moveoff.N.dbg-state s32 out
Debug output for current state of state machine
LICENSE
GPL
как это прописывается в хал:
# halfile to connect a moveoff.comp for axis gui examples
# This halfile modifies the conections made in core_sim.hal
# to add a moveoff component and addfs its functions
# This halfile must follow core_sim.hal
# moveoff offsetting component (use names=mv is required):
# addf the moveoff funcs in correct sequence:
addf mv.write-outputs servo-thread 3
addf mv.read-inputs   servo-thread 1
# modify connections set in core_sim.hal
unlinkp axis.0.motor-pos-cmd
unlinkp axis.1.motor-pos-cmd
unlinkp axis.2.motor-pos-cmd
unlinkp axis.0.motor-pos-fb
unlinkp axis.1.motor-pos-fb
unlinkp axis.2.motor-pos-fb
# connect motor-pos-cmd pins to the component:
net Xpos axis.0.motor-pos-cmd => mv.pos-0
net Ypos axis.1.motor-pos-cmd => mv.pos-1
net Zpos axis.2.motor-pos-cmd => mv.pos-2
# generated positions with offsets ADDED are
# 'short circuited' to the feedback input pins:
net mx:plus mv.pos-plusoffset-0 => mv.fb-0
net my:plus mv.pos-plusoffset-1 => mv.fb-1
net mz:plus mv.pos-plusoffset-2 => mv.fb-2
# synthesized feedback values with offsets SUBTRACTED
# are sent back to motion:
net mx:fb mv.fb-minusoffset-0 => axis.0.motor-pos-fb
net my:fb mv.fb-minusoffset-1 => axis.1.motor-pos-fb
net mz:fb mv.fb-minusoffset-2 => axis.2.motor-pos-fb
# example setting global inputs from ini file:
setp mv.epsilon              [MOVEOFF]EPSILON
setp mv.waypoint-sample-secs [MOVEOFF]WAYPOINT_SAMPLE_SECS
setp mv.waypoint-threshold   [MOVEOFF]WAYPOINT_THRESHOLD
# offset rates from ini file:
setp mv.offset-vel-0 [MOVEOFF_0]MAX_VELOCITY
setp mv.offset-vel-1 [MOVEOFF_1]MAX_VELOCITY
setp mv.offset-vel-2 [MOVEOFF_2]MAX_VELOCITY
# offset accels from ini file:
setp mv.offset-accel-0 [MOVEOFF_0]MAX_ACCELERATION
setp mv.offset-accel-1 [MOVEOFF_1]MAX_ACCELERATION
setp mv.offset-accel-2 [MOVEOFF_2]MAX_ACCELERATION
# offset min, max limits
setp mv.offset-min-0 [MOVEOFF_0]MIN_LIMIT
setp mv.offset-min-1 [MOVEOFF_1]MIN_LIMIT
setp mv.offset-min-2 [MOVEOFF_2]MIN_LIMIT
setp mv.offset-max-0 [MOVEOFF_0]MAX_LIMIT
setp mv.offset-max-1 [MOVEOFF_1]MAX_LIMIT
setp mv.offset-max-2 [MOVEOFF_2]MAX_LIMIT
# overall enable for the component:
# 1 ==> enabled as soon as apply-offsets asserted
# 0 ==> external control of move-enable required
setp mv.move-enable 0
# offset values (set as required with your gui)
setp mv.offset-in-0 0
setp mv.offset-in-1 0
setp mv.offset-in-2 0
ну и код :
component moveoff "Component for Hal-only offsets";
description
supported.
anded internally.   A \\fBwarning\\fR pin is set and a message issued if the
Applied offsets are \\fBautomatically returned\\fR to zero (respecting limits)
Backtracking through waypoints results in \\fBslower\\fR movement rates as the
When backtrack-enable is FALSE, the auto-return move is \\fBNOT\\fR
limits) and an \\fBError\\fR message is issued.
\\fBCaution:\\fR If offsets are enabled and applied and the machine is turned off
for any reason, any \\fBexternal\\fR Hal logic that manages the enabling pins
nor available in GUI preview displays.  \\fBNo protection is provided\\fR for
are not honored, an offset move may encounter hard limits (or \\fBCRASH\\fR if
the machine -- see \\fBCaution\\fR above.
hazards \\fBbefore\\fR use on hardware.
maximum is 9).
Use of the names= option for naming is \\fBrequired\\fR for compatibilty
  loadrt moveoff names=\\fBmv\\fR personality=number_of_joints
//"""" quote char for vim highlighting
Copyright: 2014-2015
Authors:   Dewey Garrett <dgarrett@panix.com>, Andy Pugh <bodgesoc@gmail.com>
This program is free software; you can redistribute it and/or modify
it under the terms of the GNU General Public License as published by
the Free Software Foundation; either version 2 of the License, or
(at your option) any later version.
This program is distributed in the hope that it will be useful,
but WITHOUT ANY WARRANTY; without even the implied warranty of
MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE.  See the
GNU General Public License for more details.
You should have received a copy of the GNU General Public License
along with this program; if not, write to the Free Software
Foundation, Inc., 59 Temple Place, Suite 330, Boston, MA  02111-1307  USA
pin in  bit power_on      "Connect to motion.motion-enabled";
pin in  bit move_enable   "Enable offsets (Enabling requires apply-offset TRUE also)";
pin in  bit apply_offsets "Enable offsets (Enabling requires move-enable TRUE also)";
pin in  bit backtrack-enable = 1 "Enable backtrack on auto-return";
pin in  float epsilon=0.0005 "When enablin pins are deactivated, return to un-offsetted position within epsilon units.  Warning: values that are too small in value may cause overshoot,  A minimum value of 0.0001 is \\fBsilently enforced\\fR";
pin in float waypoint-threshold = 0.02 "Minimum distance (in a single axis) for a new waypoint";
pin in float waypoint-sample-secs = 0.02 "Minimum sample interval (in seconds) for a new waypoint";
pin out bit warning "Set TRUE if apply-offsets is deasserted while offset-applied is TRUE";
pin out bit offset_applied "TRUE if one or more offsets are applied";
pin out bit waypoint-limit = 0 "Indicates waypoint limit reached (motion ceases), an enabling pin must be deasserted to initiate return to original position";
pin out s32 waypoint-ct "Waypoint count (for debugging)";
pin out s32 waypoint-percent-used "Percent of available waypoints used";
pin in  float offset-in-#[9 : personality] "Joint offset input value";
pin in  float pos-#[9 : personality] "Joint position (typ: axis.0.motor-pos-cmd)";
pin in  float fb-#[9 : personality] "Joint feedback (typ from encoder and input to pid controller (pid.feedback))";
pin out float offset-current-#[9 : personality]"Joint offset current value";
pin out float pos-plusoffset-#[9 : personality] "Computed joint position plus offset (typically connect to pid command input)";
pin out float fb-minusoffset-#[9 : personality] "Computed Joint feedback minus offset (typically connected to axis.0.motor-pos-fb";
pin in  float offset-vel-#[9 : personality]=10 "Joint offset velocity limit";
pin in  float offset-accel-#[9 : personality]=100 "Joint offset acceleration limit";
pin in  float offset-min-#[9 : personality] = -1e20 "Minimum limit for applied joint offset (typ negative)";
pin in  float offset-max-#[9 : personality] = 1e20 "Maximum limit for applied offset (typ positive)";
// inputs for debugging:
pin  in bit   dbg_waypoint_limit_test "Debug input to test with limited number of waypoints";
// outputs for debugging:
pin out s32   dbg_state "Debug output for current state of state machine";
option personality;
option extra_setup;
function read_inputs "Read all inputs";
function write_outputs "Write computed offset outputs\n(offset-current-M, pos-plusoffset-M, fb-minusoffset-M).\nAll other outputs are updated by read-inputs()";
license "GPL";
#include "rtapi_math.h"
#define NCHANNELS         9
#define NWAYPOINTS     1000
#define TST_NWAYPOINTS   50
#define MIN_EPSILON       0.0001
typedef enum {
  IDLE,
  MOVE_AWAY,
  MOVE_BACK,
} the_state;
typedef struct {
int state[NCHANNELS];
    hal_float_t old_in[NCHANNELS];
    hal_float_t old_out[NCHANNELS];
    hal_float_t old_v[NCHANNELS];
    hal_float_t old_limited_in[NCHANNELS];
} old_values_t;
struct lim3_input {
    hal_float_t  minlimit;
    hal_float_t  maxlimit;
    hal_float_t  maxvlimit;
    hal_float_t  maxalimit;
    hal_float_t  in;
    hal_float_t  old_in;
    hal_float_t  old_out;
    hal_float_t  old_v;
static void reset_old(int nchan, old_values_t* d) {
    int i;
    for (i = 0;i < nchan; i++) {
        d->old_in[i]         = 0;
        d->old_out[i]        = 0;
        d->old_v[i]          = 0;
        d->old_limited_in[i] = 0;
static int offset_removed(int nchan, old_values_t d, hal_float_t eps) {
    int removed = 1;
    int i;
    for (i = 0 ; i < nchan ; i++) {
        if (fabs(d.old_out[i]) > eps) {
            removed = 0;
            break;
    return removed;
static int at_waypoint(int nchan,
                       hal_float_t g[],
                       hal_float_t p[],hal_float_t eps) {
    int within_eps = 1;
    int i;
        if ( fabs(p[i] - g[i]) > eps ) {
            within_eps = 0;
            break;
    return within_eps;
static long theperiod;
static void lim3(struct lim3_input input,
                 hal_float_t* old_in,
                 hal_float_t* limited_out,
                 hal_float_t* old_v
    /* following code is adapted from limit3.comp */
    hal_float_t dt = theperiod * 1e-9;
    hal_float_t in_v, min_v, max_v, avg_v;
    hal_float_t min_out,max_out;
    hal_float_t ramp_a, match_time, est_in, est_out;
    hal_float_t err, dv, dp;
    hal_float_t limited_in;
    /* apply first order limit */
    limited_in = input.in;
    if (input.in < input.minlimit) {
        limited_in = input.minlimit;
    if (input.in > input.maxlimit) {
         limited_in = input.maxlimit;
    *old_in = limited_in;
    /* calculate input derivative */
    in_v = (limited_in - input.old_in) / dt;
    /* determine v and out that can be reached in one period */
    min_v = input.old_v - input.maxalimit * dt;
    if (min_v < -input.maxvlimit) {
        min_v = -input.maxvlimit;
    max_v = input.old_v + input.maxalimit * dt;
    if (max_v > input.maxvlimit) {
        max_v = input.maxvlimit;
    min_out = input.old_out + min_v * dt;
    max_out = input.old_out + max_v * dt;
    if (   ( limited_in >= min_out ) && ( limited_in <= max_out )
        && ( in_v >= min_v ) && ( in_v <= max_v ) ) {
        /* we can follow the command without hitting a limit */
        *limited_out = limited_in;
        *old_v = ( *limited_out - input.old_out ) / dt;
    } else {
        /* can't follow commanded path while obeying limits */
        /* determine which way we need to ramp to match v */
        if ( in_v > input.old_v ) {
            ramp_a = input.maxalimit;
        } else {
            ramp_a = -input.maxalimit;
        /* determine how long the match would take */
        match_time = ( in_v - input.old_v ) / ramp_a;
        /* where we will be at the end of the match */
        avg_v = ( in_v + input.old_v + ramp_a * dt ) * 0.5;
        est_out = input.old_out + avg_v * match_time;
        /* calculate the expected command position at that time */
        est_in = input.old_in + in_v * match_time;
        /* calculate position error at that time */
        err = est_out - est_in;
        /* calculate change in final position if we ramp in the
        opposite direction for one period */
        dv = -2.0 * ramp_a * dt;
        dp = dv * match_time;
        /* decide what to do */
        if ( fabs(err + dp*2.0) < fabs(err) ) {
            ramp_a = -ramp_a;
        if ( ramp_a < 0.0 ) {
            *limited_out = min_out;
            *old_v = min_v;
        } else {
            *limited_out = max_out;
            *old_v = max_v;
    return;
static the_state    state = IDLE;
static int          next_waypoint_index;
static rtapi_s64    last_waypoint_time;
static rtapi_s64    now;
static hal_float_t  time_since_last_sample;
static hal_float_t  move_threshold;
static hal_float_t  min_sample_interval;
static bool         backtrack;
static bool         gave_msg;
static int          max_waypoints = NWAYPOINTS;
static struct       lim3_input input;
static hal_float_t  goal[NCHANNELS];
static hal_float_t  waypoints[NCHANNELS][NWAYPOINTS];
static old_values_t data;
static hal_float_t  eps_in_use;
static bool         move_in_progress = 0;
static the_state    next_state;
//compile time setting:
static const bool   allow_backtrack_enable_change = 1;
// 1 ==> backtrack-enable can be changed while enabled
//       waypoints are always accumulated and waypoint_limit enforced
// 0 ==> backtrack-enable is sampled only while IDLE
//       if backtrack-enable == 0, no waypoints and no waypoint_limit
//       (e.g., unlimited no. of offset samples)
FUNCTION(read_inputs) {
    hal_float_t last,delta;
    int r;
    bool all_enables  = power_on && move_enable && apply_offsets;
    if (allow_backtrack_enable_change) {
      backtrack = backtrack_enable;
      // change at any time (controls auto-return)
    theperiod = period;
    now = rtapi_get_time();
    if (state == IDLE) {
        backtrack = backtrack_enable; // ref: allow_backtrack_enable_change
        // allow changes only when IDLE for these inputs:
        move_threshold = waypoint_threshold;
        min_sample_interval = waypoint_sample_secs;
        eps_in_use = epsilon;
        if (eps_in_use < MIN_EPSILON) { eps_in_use = MIN_EPSILON; }
        if (dbg_waypoint_limit_test) {
            max_waypoints = TST_NWAYPOINTS; // tiny limit for testing
        } else {
    if (backtrack || allow_backtrack_enable_change) {
        int r;
        bool sufficient_movement_for_new_waypoint = 0;
        time_since_last_sample = (hal_float_t)(now - last_waypoint_time)/1e9;
        switch (state) {
            case IDLE:
                  next_waypoint_index = 0;
                  break;
            case MOVE_AWAY:
                //note: gui must handle waypoint_limit -- here we just stop
                if (waypoint_limit) break; // no more room for waypoints
                if (time_since_last_sample < min_sample_interval) break;
                for (r=0; r < personality; r++) {
                    last  = waypoints[r][next_waypoint_index - 1];
                    delta = fabs(offset_current(r) - last);
                    if (delta > move_threshold) {
                        sufficient_movement_for_new_waypoint = 1;
                        break; //for loop
                if (!sufficient_movement_for_new_waypoint) break;
                    waypoints[r][next_waypoint_index] = offset_current(r);
                last_waypoint_time = now;
                next_waypoint_index++;
                if (next_waypoint_index > max_waypoints - 1) {
                    waypoint_limit = 1;
                } else {
                    waypoint_limit = 0;
                break;
            case MOVE_BACK: break;
    } //end save waypoints
    //{begin state control
    switch (state) {
      case IDLE:
            if ( all_enables ) {
                next_state = MOVE_AWAY;
                move_in_progress = 1;
                for (r = 0; r < personality; r++) {
                    goal[r] = offset_in(r);
            break;
      case MOVE_AWAY:
               // allow offset movements
               break;
            // one (or more) enablers is gone
            next_state = MOVE_BACK;
            if (!power_on) {
                reset_old(personality, &data);
                offset_applied = 0;
                next_state = IDLE;
                break;
                goal[r] = 0; // default (eg not waypoint backtrack)
            if (backtrack) {
                if ( next_waypoint_index > 0 ) {
                        goal[r] = waypoints[r][next_waypoint_index-1];
                    waypoint_limit = 0;
                    next_waypoint_index--;
            break;
      case  MOVE_BACK:
            if (!power_on) {
                offset_applied = 0;
                next_state = IDLE;
                break;
            if (backtrack) {
                    hal_float_t pcur[NCHANNELS];
                        pcur[r] = offset_current(r);
                    if (at_waypoint(personality, goal, pcur, eps_in_use)) {
                            goal[r] = waypoints[r][next_waypoint_index];
                } else {
                        goal[r] = 0; //final goal
            if (!offset_applied) {
                // offsets gone, return to IDLE
                next_state = IDLE;
            break;
    if (   !apply_offsets
        &&  offset_applied
        warning = 1;
        if (!gave_msg) {
            // apply_offsets deasserted while offset_applied
            // for example:
            //   1) program stopped with offsets applied
            //   2) (no *.resume-inhibit pin) or (-no_resume_inhibit option)
            //      and program resumed with offsets applied
                rtapi_print_msg(RTAPI_MSG_ERR,
                           "Index: %i, offset=%f",
                           r, data.old_out[r]);
            "apply_offsets deasserted before offsets removed "
            "moveoff.comp: WARNING"
            gave_msg = 1;
    } else {
        gave_msg = 0;
        warning = 0;
    //}end state control
} //read_inputs
FUNCTION(write_outputs) {
    int r;
    // move with limits on postion, velocity, acceleration
        if (move_in_progress) {
            input.in = goal[r];
            input.minlimit   = offset_min(r);
            input.maxlimit   = offset_max(r);
            input.maxvlimit  = offset_vel(r);
            input.maxalimit  = offset_accel(r);
            input.old_in     = data.old_in[r];
            input.old_out    = data.old_out[r];
            input.old_v      = data.old_v[r];
            if ( waypoint_limit && (state == MOVE_AWAY) ) {
                // no movement in MOVE_AWAY (require: remove enable)
            } else {
                hal_float_t last_old = data.old_out[r];
                lim3(input,
                     &data.old_in[r],
                     &data.old_out[r],
                     &data.old_v[r]
                offset_current(r) = data.old_out[r];
                fb_minusoffset(r) = fb(r)  - offset_current(r)
                                  - (last_old - data.old_out[r]);
                pos_plusoffset(r) = pos(r) + offset_current(r);
        } else {
            pos_plusoffset(r) = pos(r);
            offset_current(r) = 0;
            fb_minusoffset(r) = fb(r);
    offset_applied = ! offset_removed(personality, data, eps_in_use);
    if ( !offset_applied ) {
        // reset backtrack
        waypoint_limit = 0;
    waypoint_ct = next_waypoint_index;
    waypoint_percent_used = 100*next_waypoint_index/max_waypoints;
    dbg_state = state;
    state = next_state;
} //write_outputs
EXTRA_SETUP() {
    if (personality == 0) personality = 3;
    return 0;
Re: Moveoff
Добавлено: 05 июл 2015, 23:30
вот что сразу не увидел , запуская примеры:
компонент работает в режиме JWP(jog во время паузы)...
то есть - не прерывая выполнения программы (поставив на паузу) мы можем сделать отступ по любой оси...
емс должен "отработать" введенную поправку с задаными скоростью и ускорением
вот только величина оффсета не появляется в DRO ...
может это из-за примеров именно в sim????
Re: Moveoff
Добавлено: 06 июл 2015, 07:53
стоит отметить несколько нововведений в devel-версии емс...
новый раздел в INI файле - секция [APPLICATIONS]
"организует" запуск сторонних приложений
и тут же компонент sim_pin
удобная штука - для отладки всегда лепим свои панельки ...
кнопки на панельке работают в трех "режимах":
стабатывание по фронту,
"залипание",
и "пока держим"
Выделение_003.png (4082 просмотра) <a class='original' href='./download/file.php?id=53596&mode=view' target=_blank>Загрузить оригинал (66.47 КБ)</a>
зы
маленький штрих:
не срабатывает с пробелом вот здесь:
можно долго искать причину "неисправности" в таком случае :)
Re: Moveoff
Добавлено: 06 июл 2015, 09:30
следующие строки :
говорят о том ,что функции будут выполняться в потоке в установленом порядке(1,3)
    'thread_name' is the name of the thread to which the function
    should be added.  When the thread runs, the functions will
    be executed in the order in which they were added to the
    thread.
    'position' is the desired location within the thread. This
    determines when the function will run, in relation to other
    functions in the thread.  A positive number indicates the
    desired location as measured from the beginning of the thread,
    and a negative is measured from the end.  So +1 means this
    function will become the first one to run, +5 means it will
    be the fifth one to run, -2 means it will be next to last,
    and -1 means it will be last.  Zero is illegal.
    Returns 0, or a negative error code.    Call
    only from within user space or init code, not from
    realtime code.
если в объявлении функции не указана очередность,
(строки вида addf mv.read-inputs servo-thread)
то выполнятся они будут в порядке объявления...
вот интересно : и первый раз тоже???
то есть -
сначала читаем файл(функции не выполняем!),
потом "расставляем" функции "по местам" в потоке ,
и лишь затем начинаем выполнять...
Re: Moveoff
Добавлено: 06 июл 2015, 09:41
nkp писал(а):до конца еще не понял как он работает ,поэтому оставлю здесь по нему информацию
Скорее всего просто встановиться в цепочки
axis.pos-cmd   -> (вот сюда) -> stepgen.pos-cmd
stepgen.pos-fb -> (сюда) -> axis.pos-fb
Потому в DRO и не отображаются перемещения.
nkp писал(а):маленький штрих:
Это скорее всего экранирование переноса строки. (если в конце строки ставишь \, то перенос строки игнорируется, а если после \ поставить " ", то он уже не будет игнорироваться, в bash и sh вроде так (в том числе в консоле)).
Лучше просто в одну строку напиши все пины и все ;).
nkp писал(а):вот интересно : и первый раз тоже???
Скорее всего да.
А зачем тебе?
Мне вот интересно как будет работать
addf mv.write-outputs servo-thread 1
addf mv.read-inputs   servo-thread -2
и
addf mv.write-outputs servo-thread -2
Re: Moveoff
Добавлено: 06 июл 2015, 10:14
Nick писал(а):Лучше просто в одну строку напиши все пины и все
если пинов немного - конечно...
а вот если много - удобней так...
а про пробел для других написал - мало ли ;)
Nick писал(а):Мне вот интересно как будет работать
не - если
addf mv.read-inputs   servo-thread -1
то есть первая от начала 1
и первая с конца -1
думаю будут выполнятся как равнозначные - то есть по очереди объявления
а у тебя в примере :
сначала -2
потом 1
?? :thinking:
Nick писал(а):Скорее всего просто встановиться в цепочки
ну тогда это только на один сеанс(без сохранения)
и контролировать как визуально - что там мы "наотступали"??
Re: Moveoff
Добавлено: 06 июл 2015, 11:02
nkp писал(а):ну тогда это только на один сеанс(без сохранения)
так там свой гуи вроде есть отдельный.
Re: Moveoff
Добавлено: 06 июл 2015, 12:06
Nick писал(а):так там свой гуи вроде есть отдельный.
не "держится" в нем ничего
вроде бы :thinking:
ну я уже говорил - не разобрался до конца еще ;)
Re: Moveoff
Добавлено: 06 июл 2015, 12:13
А зачем хранить, нажал паузу, поехал куда надо в своем gui, потом сказал, ехать назад, и снял паузу (кстати у него на сколько я понял есть вариант автоматического снятия с паузы).
Самое не приятное, на сколько я понял, можно только перемещаться дополнительным оффсетом, Gкод выполнять нельзя, т.е. G38 нельзя сделать для обнуления нового инструмента.
Re: Moveoff
Добавлено: 06 июл 2015, 12:17
Наверняка это работает очень просто:
1 означает вставить функцию в начало списка.
2 - вставить функцию после первой.
-2 - вставить функцию после второй с конца
и т.п.
Например после выполенения
addf f1 servo-thread 1
addf f2 servo-thread 1
addf f3 servo-thread
addf f4 servo-thread -2
addf f5 servo-thread -2
получится такая последовательность:
f2
f1
f4
f5
f3
Re: Moveoff
Добавлено: 06 июл 2015, 12:21
Тоже так подумал, но тогда
addf f1 servo-thread 2
даст f1,f2 вместо ожидаемых f2,f1
Re: Moveoff
Добавлено: 06 июл 2015, 12:24
UAVpilot писал(а):Наверняка это работает очень просто:
можно даже написать в компонент несколько функций и проверить в разных вариациях...
так как ты показал - вроде бы наиболее логично...
но совсем неочевидно ...
и если функций с десяток и вперемешку "номера загрузки" - без листочка с карандашом
и не разберешся :)
Re: Moveoff
Добавлено: 06 июл 2015, 12:28
Nick писал(а):даст f1,f2 вместо ожидаемых f2,f1
Должно получится f2,f1.
nkp писал(а):без листочки с карандашом
и не разберешся :)
Оно придумано не для упорядочивания всех функций, а для вставки в нужное место некоторых...
Re: Moveoff
А зачем писать, можно взять stepgen или parport :)
Re: Moveoff
Добавлено: 06 июл 2015, 12:33
расскажи - как?
там же мало функций ...
Re: Moveoff
Добавлено: 06 июл 2015, 12:41
UAVpilot писал(а):Оно придумано не для упорядочивания всех функций, а для вставки в нужное место некоторых...
ну может быть и так ;)
но это не одно ли и тоже? значит я не чувствую в определении различия :hehehe:
то есть - обычно функции не нумеруют , и они выполняются "по порядку" - как прописаны...
вот нам вдруг потребовалось добавить некую функцию ,и она должна строго
отрабатывать после(до) определенной ,уже существуюшей функции...
Re: Moveoff
Добавлено: 06 июл 2015, 12:49
nkp писал(а):расскажи - как?
Можно даже без них:
loadrt trivkins
loadrt motmod servo_period_nsec=1000000 num_joints=3
show funct
addf motion-command-handler servo-thread 1
halcmd: addf motion-controller servo-thread 2
PS проверил, если сразу написать:
addf motion-command-handler servo-thread 20
то скажет
halcmd: addf motion-command-handler servo-thread 20
HAL: ERROR: position '20' is too high
<stdin>:6: addf failed
:tongue:
Re: Moveoff
Добавлено: 06 июл 2015, 14:41
nkp писал(а):но это не одно ли и тоже? значит я не чувствую в определении различия :hehehe:
Понимаешь неправильно.
Это не для того, чтобы все функции выстраивать в определённом порядке, а для того, чтобы некоторые, которые можно загрузить только на определённом этапе можно было поставить в начало или в конец очереди. Например HAL-файл, который надо загружать в начале (содержит определение сигналов) может добавить функцию, которую надо исполнять в конце очереди...
nkp писал(а):вот нам вдруг потребовалось добавить некую функцию ,и она должна строго
В этот момент мы можем поместить её в нужно место в очереди определив взаимное расположение этих двух функций в очереди. Однако последующие добавления других функций в очередь изменят саму очередь, но взаимное расположение тех двух функций в очереди (какая после какой) не изменится, хотя между ними и могут появится другие функции.
Re: Moveoff
Добавлено: 06 июл 2015, 14:47
такая система потока применяется еще где то???
просто ты так уверенно чеканишь определения,но про емс в этом контексте точно нигде не написано :shock:
(ну может только комменты в исходниках :) )
Re: Moveoff
Добавлено: 06 июл 2015, 15:34
Я не уверен, что в LinuxCNC именно так работает, но считаю это наиболее вероятным вариантом по косвенным причинам:
1. Можно несколько раз написать "addf чего-то-там servo-thread 2" и оно не ругается, что 2 уже занято.
2. Иначе пришлось-бы конкретно переписать эту часть в LinuxCNC, а это я бы заметил. :)
Подобный механизм много где применяется, например при добавлении правил в iptables (firewall в Linux).