LINUXCNC - 2.8.0-pre1-598-g048366b
Machine configuration directory is '/home/user/linuxcnc/configs/my1'
Machine configuration file is 'my1.ini'
Starting LinuxCNC...
Found file:./my1.hal
Found file:./custom.hal
spindle-vfd: device='/dev/ttyUSB0', baud=9600, bits=8, parity='none', stopbits=1, address=1, verbose=1, PID=5684
Opening /dev/ttyUSB0 at 9600 bauds (none)
HALDATA=>enable - gooD!!!!
Func. read_setup: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)
Func. read_setup: FAILED!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [B77C1DF8]
response data = [0000]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [B77C1DF8]
response data = [0000]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [B77C1DF8]
response data = [0000]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [B77C1DF8]
response data = [0000]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [B77C1DF8]
response data = [0000]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [B77C1DF8]
response data = [0000]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][01][01][F4][D3][DD]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][01][01][F4][D3][DD]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][06][20][00][00][00][82][0A]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][00][82][0A]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][06][00][01][64][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]
Func. read_data: OK!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
read return = [08] bytes
msg_length = [08]
characters received =[01][06][50][01][00][05][09][09]
crc check = 00
we received a message of [08] bytes, with a valid crc
the message function code is = [06]
response parameter = [5001]
response data = [0005]
Func. write_data: OK!
Func. read_data: Reading parameters...

query_length = 6
Modbus query = [01][03][00][01][00][01][D5][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][02][00][01][25][CA]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][0E][D8][BC][7E]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][03][00][01][74][0A]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][04][00][01][C5][CB]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
read return = [07] bytes
msg_length = [07]
characters received =[01][03][02][00][00][B8][44]
crc check = 00
we received a message of [07] bytes, with a valid crc
the message function code is = [03]
response parameter = [5001]
response data = [0005]

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][03][00][05][00][01][94][0B]
query_ret = 8
response_length_computed = 7
waiting for message (7 bytes)...
length to read = 7
WAIT_DATA(): comms time out

ERROR Communication time out (-12)
Func. read_data: FAILED!
Func. write_data: Writing parameters...
VFD: set_spindle_speed=0.000000, abs_freq=0

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAIT_DATA(): comms time out

ERROR Communication time out (-12)

query_length = 6
Modbus query = [01][06][20][00][00][01][43][CA]
query_ret = 8
response_length_computed = 8
waiting for message (8 bytes)...
length to read = 8
WAITShutting down and cleaning up LinuxCNC...
Xlib.protocol.request.QueryExtension
Xlib.protocol.request.QueryExtension
Running HAL shutdown script